Heating garage

Started by Silver R/T, December 13, 2011, 08:07:22 PM

Previous topic - Next topic

Silver R/T

I'd like to get some projects done in winter months so I want to buy tank mounted propane heater 30K BTU and heat my 3 car garage. Should I be fine with that or there's something I'm overlooking?
http://www.cardomain.com/id/mitmaks

1968 silver/black/red striped R/T
My Charger is hybrid, it runs on gas and on tears of ricers
2001 Ram 2500 CTD
1993 Mazda MX-3 GS SE
1995 Ford Cobra SVT#2722

jb666

Ventilation.

The tank mount propane heaters will kill you. If you're going to crack your door, that's fine, it'll let some fresh air in.

Another thing is , one of those will raise your garage from 30-70 degrees in minutes, but it'll also make everything in there sweat.. 




Silver R/T

I plan on running 2 window fans 2500cfm each.
http://www.cardomain.com/id/mitmaks

1968 silver/black/red striped R/T
My Charger is hybrid, it runs on gas and on tears of ricers
2001 Ram 2500 CTD
1993 Mazda MX-3 GS SE
1995 Ford Cobra SVT#2722

jb666

Quote from: Silver R/T on December 13, 2011, 09:30:48 PM
I plan on running 2 window fans 2500cfm each.
You should be all set in that area...

I'm not sure what your climate is, but in my area, when I was running them (oversized 2 car) my biggest problem was the condensation this type of heater caused. It was horrible, the cars would almost be dripping wet.

johnnycharger

If these condensate too much....what is the best type of heater to use for a three car garage? 

The70RT

A heated floor is probably best then natural gas. I use wood it is cheap, you just have to have common sense and have it installed correctly.  :Twocents:
<br /><br />Uploaded with ImageShack.us

jb666

Quote from: johnnycharger on December 13, 2011, 09:47:09 PM
If these condensate too much....what is the best type of heater to use for a three car garage? 

It all depends what you have accessible for a power source out there?  I switched to an in-wall 30k BTU heater/AC unit(240V). It's been in for two seasons now. AMAZING heat and ice cold AC... Combined with insulation head to toe and that room is the most 'climate controlled' I have!


A383Wing

I have an old house furnace that runs on diesel...got a 5 gallon container that it sucks the fuel from and dumps the overflow back into....heats my 5 car garage nicely, uses about 5 gallons per day if I run it all day. Hot air comes out the bottom and exhausts through the roof

Bryan







69 OUR/TEA

Quote from: The70RT on December 13, 2011, 09:50:15 PM
A heated floor is probably best then natural gas. I use wood it is cheap, you just have to have common sense and have it installed correctly.  :Twocents:


    :yesnod: :2thumbs:

Silver R/T

That sucks about moisture. I was planning on painting parts during winter.
http://www.cardomain.com/id/mitmaks

1968 silver/black/red striped R/T
My Charger is hybrid, it runs on gas and on tears of ricers
2001 Ram 2500 CTD
1993 Mazda MX-3 GS SE
1995 Ford Cobra SVT#2722

mrsskip68

This is a Kerosene heater Chuck uses for our garage. We dont need to run it more than a couple minutes to warm it up. Smells a little bit, but we do have ventilation! It really works dam well for our situation.  :Twocents:

Lisa

Silver R/T

Ya I was considering kerosene heater but figured propane would be cheaper to run. Didn't know about whole condensation situation.
http://www.cardomain.com/id/mitmaks

1968 silver/black/red striped R/T
My Charger is hybrid, it runs on gas and on tears of ricers
2001 Ram 2500 CTD
1993 Mazda MX-3 GS SE
1995 Ford Cobra SVT#2722

ITSA426

I have in floor heat and think it's the best way to go.  It's quiet and odor free.  It heats the concrete at night at off peak electric rates so the operating cost isn't bad.  The only moisture issues are melting ice from bringing in snow covered cars.  I keep the floor mopped up if it gets wet.

I've used 110 volt electric far infra red heat panels in the ceiling but it wasn't as good as advertised.  Factory reps were out several times to figure out why it wasn't working as promised.  It's probably a good supplemental system but can't stand alone in our Minnesota climate.  It cost a lot to run.  It's big claim was efficiency.

Domino


stripedelete

Is it a finished garage or bare studs?  How high is the ceiling?

64dartgt


My friend has a wood stove in his, if you don't have room you could try one of these.  It is a nice addition

http://www.northerntool.com/shop/tools/product_200446397_200446397

Iceyone

I ran pex tubing throughout the floor of what will hopefully be my new garage soon. Waiting for the contractor to begin building. I plan on using an electric water heater for the heat source. Also ran pex throughout my basement floor. House is done but haven't hooked up the floor in the basement yet. The plan for the house is to use a wood fired outdoor boiler. My shop has a wood stove which I keep fired up 24/7 during the winter months. Also have a 110K BTU kerosene heater which works very well but will make your eyes water after awhile. I did notice last winter that some of the farm supply stores around here were selling indoor propane heaters which are "supposed" to be safe for indoor use.   :Twocents:
68 Charger
70 Super Bee
11 SRT8 Challenger
30 Chevy Universal

nh_mopar_fan

Quote from: 64dartgt on December 14, 2011, 07:53:42 AM

My friend has a wood stove in his, if you don't have room you could try one of these.  It is a nice addition

http://www.northerntool.com/shop/tools/product_200446397_200446397

That's pretty cool but pricey...

Bobs69

Quote from: The70RT on December 13, 2011, 09:50:15 PM
A heated floor is probably best then natural gas. I use wood it is cheap, you just have to have common sense and have it installed correctly.  :Twocents:

I know a guy who opened his own shop, wanted to be his own boss.  He has the heat in the floor.  Says it works good, takes awhile to recover heat after the door has been opened.  Also, no furnace or anything taking up floor space!  Plus I would suspect that having the heat in the floor would be nice on your feet and joints in your legs if you were standing in there a long time.  You gotta figure the cold from the concrete would get into your legs and eventually cripple you up some.

I remember back in college a friend's father had a double garage attached to the house and heated it with a wood stove.  It was nice.  I like it and would love to do that in mine too.  It's just that the stove needs so much clearance behind, above in front.  I couldn't spare the floor space.

NHCharger

I have a 75k BTU Hot Dawg. Paid $1,200.00 installed six years ago with a 10 year warrenty.

As mentioned the condensation would only be an issue if you left the garage unheated, and then turned the heat on and have the temperature come up fast. That use to happen to me at our old house when I would work on the Charger during the winter and used a torpedo heater. Now I can leave the temp at 45º-47º, and turn the Hot Dawg up to 56º when I work in the shop, no moisture problems.Obviously when I paint I turn the temp up higher.
72 Charger- Base Model
68 Charger-R/T Clone
69 Charger Daytona clone
79 Lil Red Express - future money pit
88 Ramcharger 4x4- current money pit
55 Dodge Royal 2 door - wife's money pit
2014 RAM 2500HD Diesel

The70RT

Quote from: NHCharger on December 14, 2011, 10:25:21 PM
I have a 75k BTU Hot Dawg. Paid $1,200.00 installed six years ago with a 10 year warrenty.

As mentioned the condensation would only be an issue if you left the garage unheated, and then turned the heat on and have the temperature come up fast. That use to happen to me at our old house when I would work on the Charger during the winter and used a torpedo heater. Now I can leave the temp at 45º-47º, and turn the Hot Dawg up to 56º when I work in the shop, no moisture problems.Obviously when I paint I turn the temp up higher.

18" clearance sides, back, plus stove size.
<br /><br />Uploaded with ImageShack.us

64dartgt

Quote from: Iceyone on December 14, 2011, 08:16:01 PM
I ran pex tubing throughout the floor of what will hopefully be my new garage soon. Waiting for the contractor to begin building. I plan on using an electric water heater for the heat source. Also ran pex throughout my basement floor. House is done but haven't hooked up the floor in the basement yet. The plan for the house is to use a wood fired outdoor boiler. My shop has a wood stove which I keep fired up 24/7 during the winter months. Also have a 110K BTU kerosene heater which works very well but will make your eyes water after awhile. I did notice last winter that some of the farm supply stores around here were selling indoor propane heaters which are "supposed" to be safe for indoor use.   :Twocents:

I bought one of these http://www.amazon.com/Mr-Heater-F232000-Indoor-Safe-Portable/dp/B002G51BZU/ref=sr_1_1?ie=UTF8&qid=1323956077&sr=8-1

I figured for the price I would try it.  I plan to use it to just take the chill off when working in the garage, when working on the boat in winter, tailgating and as an emergency heat source indoors.  It is well made and easy to light as it has a built in igniter.  So far I have only used it tailgating.  In the open it only warms what is in front of it, but it worked well.  At 9000 btu's it likely won't heat my 3 car garage, but as haven't done any work on the cars in winter to date, I thought it would be worth a try to see if I can get something done out there.  Hopefully it will take the chill off.  If it works some and if I actually do some work out there I will take the next steps and start insulating and perhaps look into a large ceiling mount electric heater to save floor space.

Old Moparz

Quote from: nh_mopar_fan on December 14, 2011, 08:42:19 PM
Quote from: 64dartgt on December 14, 2011, 07:53:42 AM

My friend has a wood stove in his, if you don't have room you could try one of these.  It is a nice addition

http://www.northerntool.com/shop/tools/product_200446397_200446397

That's pretty cool but pricey...


Wow, I never knew they made such a thing.   :2thumbs:

Something to consider with this is that if it simply slides into the window, you probably don't need a permit & a C.O. to use it. I bet the building department sees as being no different than using a portable heater or window air conditioner. The 24,000 btu's is pretty high, too.

I would seriously consider this for my garage situation. In New York state you need to follow the energy code to install a heating system, even in a garage. For me that means I'd have to insulate the entire building to the R value they now require, then drywall, paint, etc. No way I'm going to do all that without roughing in plumbing, electric & more, not to mention I'd have to empty the building to do it.  :o
               Bob               



              Going Nowhere In A Hurry

PocketThunder

Quote from: NHCharger on December 14, 2011, 10:25:21 PM
I have a 75k BTU Hot Dawg. Paid $1,200.00 installed six years ago with a 10 year warrenty.

As mentioned the condensation would only be an issue if you left the garage unheated, and then turned the heat on and have the temperature come up fast. That use to happen to me at our old house when I would work on the Charger during the winter and used a torpedo heater. Now I can leave the temp at 45º-47º, and turn the Hot Dawg up to 56º when I work in the shop, no moisture problems.Obviously when I paint I turn the temp up higher.

:iagree: :iagree: :iagree:
"Liberalism is a disease that attacks one's ability to understand logic. Extreme manifestations include the willingness to continue down a path of self destruction, based solely on a delusional belief in a failed ideology."

nh_mopar_fan

Quote from: Old Moparz on December 15, 2011, 09:15:24 AM
Quote from: nh_mopar_fan on December 14, 2011, 08:42:19 PM
Quote from: 64dartgt on December 14, 2011, 07:53:42 AM

My friend has a wood stove in his, if you don't have room you could try one of these.  It is a nice addition

http://www.northerntool.com/shop/tools/product_200446397_200446397

That's pretty cool but pricey...


Wow, I never knew they made such a thing.   :2thumbs:

Something to consider with this is that if it simply slides into the window, you probably don't need a permit & a C.O. to use it. I bet the building department sees as being no different than using a portable heater or window air conditioner. The 24,000 btu's is pretty high, too.

I would seriously consider this for my garage situation. In New York state you need to follow the energy code to install a heating system, even in a garage. For me that means I'd have to insulate the entire building to the R value they now require, then drywall, paint, etc. No way I'm going to do all that without roughing in plumbing, electric & more, not to mention I'd have to empty the building to do it.  :o

I have to agree. After thinking it over, this seems like a great option.